Rick
My Hayward Heat Pump won't heat the water. Temp setting at 95 ambient temp is 85-90. Warm air coming out of the top of the heat pump. Cleaned pool pump filters, cycled the power, cleaned evap coils with a water hose from the inside. Heat pump is running and no code alarms in. Any other suggestions?
Quote
Asa
Warm air coming from the top while compressor is functioning would suggest a freon leak.  I am sure you hear the fan functioning, but is the compressor running.  If so possible freon leak.  If fan running but not compressor, than you have a compressor issue.
Quote
Brian
It could just be a bad run capacitor for the compressor.
Quote